Not per code, but safe?
junkhound
Renton, WA
EE, power electronics specialty
Grand-daughter moved into a house with well.
Power to well (circa 1950s or earlier, revised sometme in the past) is 12-2 wg UF wired for 240 V. There appears to be an abandoned MC coming into the well pit but is dead and cannot trace as buried 5 ft deep.
I added red tape to the white wire in the well pit and main breaker box, etc. which had never been done, etc, etc - some other items such as NM in well pit needed correcting etc, etc. Am not going to go to the expense of running 4 wires to the well pit, will leave the 12-2 UF as is.
The other item is that there is a shed another 30 feet away fed with black and white thru 3/4 RMC. The black to black, the white is tied to ground wire in the well pit, and the 3/4 RMC also tied to the 60ft deep 6" well casing so htat is a very solid ground point.
The NON code part is at the shed which uses the UF ground as return, The RMC is tied to the metal box, but the white is treated as a white although the only connection the main breaker panel white in the house is thru the 12-2 WG ground wire.
Other than being not per code, why is this not safe other than being non-standard?
Only thing I can think that could cause an issue is the UF ground isn't really insulated it has the thick sheath but since it's carrying current you'd want that to have an insulated path from that point on.
I'm for you getting the 4 wires there. Maybe do a 30 or 40 amp subpanel in 1/2 inch rigid to the shed and then re feed the well from that. Having water and live grounds is not ideal.
I would not be comfortable with it. If for any reason you lost the EGC you stand the chance of energizing the area around the well casing with feed back voltage from the shed.
So if I'm understanding the setup, the shed is being fed from the well. And the shed is using the well pipe as its grounding electrode.
And one of the legs of the 240v well pump is the power for the shed ran through rmc with two conductors, using rmc as the bonding between shed and well casing.
So if a fault occurs in the shed, the effective ground fault return path would be the rmc to the well and then the ground wire of the 240v circuit uf.
And the same ground wire in the uf is carrying the return current of the shed and if anyone removes that ground wire in the panel they can become in series with the circuit.
Other than a ground wire carrying current, you've made two connections to the earth. So in that regard it's similar to having the bonding screw installed in the shutoff of a remote building. (I think that's a violation, not sure off top of head, but I think you don't connect bonding screw at remote buildings due to lightning gradients)
Im not a big fan of the rmc as the ground fault return path either, (assuming its buried and you can't see what condition it's in)
To sum it up, you are one wire (or electrical path) failing away from a dangerous situation.
Good point - if they move and resell the property, will siply remove all conductors to the shed. In the meantime, till then, will put white tape on the UF ground wire just in case anyone else gets into the panel <G>
Multiple earthing of grounding conductors is perfectly okay.
A grounded conductor (neutral) should not be bonded again.