Alternating operation of 2 motors daily

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
There are two 208V 3-phase 3HP motors that I would like to alternate power daily. Let's call them motor 'A' and motor 'B'

For example,

motor 'A' will run on day 1, 3, 5, 7 and so on...
motor 'B' will run on day 2, 4, 6, 8 and so on...

There are multiple methods of doing this but I want an efficient and safe method. These motors will be fed by the same circuit and will be non-coincident load. For this reason I want to ensure the motors do not run at the same time.

I was thinking of using two VFDs (1 for each motor) and interlocking it with an external digital time clock so that it cycles the motors. I am not sure if this is a good method because I am afraid that someone will tamper with the VFD and time clock and cause both of the motors to be running at the same time which is what I'm trying to avoid.

Is using VFDs with external digital time clock a good idea for what I'm trying to do? Let me know if you have any recommendations.
 
Last edited:

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
A cheap and easy way would be to use an alternating relay. Used a lot for alternating sewage lift station pumps. Use a 24 hour timer to trigger the alternating.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Whatever scheme you come up with can be tampered with. There is no way you can prevent it.

In any case what happens if one of the motors fails? You probably want to have some way to switch it to the other one. Otherwise someone will have to tamper with it in the dead of the night to get it running.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If you do t need to vary the speed, don’t put in a VFD.

What tells the motor(s) to turn on and off now? If it’s a manual process, just put in a double throw safety switch. If it is automated, use mechanically interlocked contactors.
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
If you do t need to vary the speed, don’t put in a VFD.

What tells the motor(s) to turn on and off now? If it’s a manual process, just put in a double throw safety switch. If it is automated, use mechanically interlocked contactors.
I want to make them run with a pressure transducer. so basically it would need to be controlled by a pressure transducer and alternate operation. can I interlock them with a VFD, pressure transducer and a time clock?
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
These are made to alternate motors every run cycle. We used them alot for pump stations

But what if I need to run them on a pressure transducer, and at the same time alternate them daily?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
But what if I need to run them on a pressure transducer, and at the same time alternate them daily?
The transducer is wired ahead of the relay, the relay just selects which pump to run. The input to the relay comes from the time clock. Or even since you are using a vfd, the relay can be wired to the “enable” input on the vfd.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
But what if I need to run them on a pressure transducer, and at the same time alternate them daily?
You can make the pt signal an input to both vfds and just select one of the VFDs to run.

Personally, I would have a four way switch that would allow me to select which VFD was used, select auto for alternating, and off to turn off both. Maybe even some way to turn on both.
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
The transducer is wired ahead of the relay, the relay just selects which pump to run. The input to the relay comes from the time clock. Or even since you are using a vfd, the relay can be wired to the “enable” input on the vfd.
So if input 1 is on it will close contact 1 and if input 2 is on it will close contact 2?
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
But what if I need to run them on a pressure transducer, and at the same time alternate them daily?
You'll have to read the specs on them. The ones I worked with were quite a bit older. I know the ones I put in ran two pumps. Every time a float switch closed it would start a pump. when the water level went down and the float switch opened it shut off the pump. When the level rose again it would start the other pump. There was also another float switch for when the level got too high it would run both pumps. That float switch also served as a backup system so if one pump failed the other pump would run.

I had air compressors on a similar control years ago that was pre electronic all mechanical.

What you have is not an unusual situation. There have been controls on the market to do this for probably 100 years.

Google "Alternating Relay" or Alternating Control" and you'll find lots of products
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Don't forget you'll need to program a dead band into the controller somehow. You don't want to switch motors while one of them is running.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I want to make them run with a pressure transducer. so basically it would need to be controlled by a pressure transducer and alternate operation. can I interlock them with a VFD, pressure transducer and a time clock?
Ok, pressure transducer operations and a VFD adds complexity to this. The transducer would provide a variable signal, good for telling a VFD what speed to run, but the on-off decision then needs some intelligence involved. Some VFDs can likely do this, others cannot, so without info on what VFD you plan on using it’s difficult to tell.

Personally I would put a micro PLC into the mix and have it control a couple of mechanically interlocked contactors on the output of one VFD, with the appropriate safeguards to prevent the contactors from opening or closing under load. Alternatively you could use two VFDs, one for each motor, but depending on the HP we are talking about here, that might cost a lot more.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
If you haven't figured it out by the responses you have gotten, how this kind of thing can be handled could vary a lot, and probably the end solution will be determined largely by factors you have not bothered to tell us, and might not have even considered yourself, cost and complexity being just two of the factors.
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
Ok, pressure transducer operations and a VFD adds complexity to this. The transducer would provide a variable signal, good for telling a VFD what speed to run, but the on-off decision then needs some intelligence involved. Some VFDs can likely do this, others cannot, so without info on what VFD you plan on using it’s difficult to tell.

Personally I would put a micro PLC into the mix and have it control a couple of mechanically interlocked contactors on the output of one VFD, with the appropriate safeguards to prevent the contactors from opening or closing under load. Alternatively you could use two VFDs, one for each motor, but depending on the HP we are talking about here, that might cost a lot more.
is something like this acceptable? I just drew it.
IMG_8882.jpg

M1 and M2 on the ladder logic is the coils for motor M1 and M2
 