I am building a detached garage. I planned to have no electrical or plumbing to keep the cost down.
When I applied for my permit, they approved my building plans, but then I got a call from the building dept. They said I did not list an electrician on the permit declaration form. I told them I do not have any plans to install electircal wiring in the garage.
The guy told me that the 2017 NEC requires detached garage to have at least one branch circuit.
he said section 210.11 C.4 states this so I have to run a branch wire out to the garage.
here it is:
(4) Garage Branch Circuits. In addition to the number of
branch circuits required by other parts of this section, at least
one 120-volt, 20-ampere branch circuit shall be installed to
supply receptacle outlets in attached garages and in detached
garages with electric power. This circuit shall have no other
outlets.
The way I read that section you must have a branch circuit to the garage IF it has electical power.
Does anyone know, is the code saying you don't have a choice and detched garage must have electical power.
or as I see it, you must use a branch circuit if you install electrical power in the garage. .
When I applied for my permit, they approved my building plans, but then I got a call from the building dept. They said I did not list an electrician on the permit declaration form. I told them I do not have any plans to install electircal wiring in the garage.
The guy told me that the 2017 NEC requires detached garage to have at least one branch circuit.
he said section 210.11 C.4 states this so I have to run a branch wire out to the garage.
here it is:
(4) Garage Branch Circuits. In addition to the number of
branch circuits required by other parts of this section, at least
one 120-volt, 20-ampere branch circuit shall be installed to
supply receptacle outlets in attached garages and in detached
garages with electric power. This circuit shall have no other
outlets.
The way I read that section you must have a branch circuit to the garage IF it has electical power.
Does anyone know, is the code saying you don't have a choice and detched garage must have electical power.
or as I see it, you must use a branch circuit if you install electrical power in the garage. .