Ryancbell121
Member
- Location
 - Pennsylvania
 
- Occupation
 - Master Electrician
 
I have installed generator interlock kits for 200 amp residential services and portable generators.  I want to install 2 interlock kits on each 200 amp main panel of a 400 amp residential service.  I will splice the conductors from the generator inlet to each panels interlock breaker.  
Is there any issue with this? I read an another forum and people were saying that you have neutrals going to each panel, I dont see the problem with that since the current flows back to the generator and not on the Service neutral.
	
		
			
		
		
	
				