electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Sanity check - Any issue here? What is the accessibility classification? Assume not a GFCI recep and not a disconnecting means.
The way I read that, if the recep/plug is serving as the disconnecting means, it needs to be accessible. Based on the definition of accessible, I think the receptacle could be behind the dishwasher, EVEN IF it was serving as the disconnecting means.Must be accessible or have disconnecting means! 422.33
Where is that stated?Receptacles are required to be accessible not readily accessible.
It looks like flexible cord connections for specific appliances are covered in 422.16(B). The appliances called out seem to be allowing an “accessible” vs. “readily accessible “receptacle. A dishwasher receptacle is no longer permitted to be located in the appliance space- NEC 422.16(B)(2)(5)Where is that stated?
I can't imagine that.would the dishwasher once mounted be part of the stated " finish of the building"
I think the accessibility requirement for a receptacle falls under equipment vs. a wiring methodAccessible means you can get to it without damaging walls, etc.
Readily accessible means you can quickly put your hands on itView attachment 2567002
yes but the appliance is still in place when you access it. You can't do that with the dish. I think its a battle with inspector if you try and put it behind the dish.I can't imagine that.
There are other appliances which have cords and require some amount of disassembly to access.
I'm thinking about some wall mounted range hoods, where receptacle is behind a shroud.
was wondering about that also.I think the accessibility requirement for a receptacle falls under equipment vs. a wiring method
What exactly is a "built in dishwasher"?It looks like flexible cord connections for specific appliances are covered in 422.16(B). The appliances called out seem to be allowing an “accessible” vs. “readily accessible “receptacle. A dishwasher receptacle is no longer permitted to be located in the appliance space- NEC 422.16(B)(2)(5)
never seen one of those so I looked on page 44 shows the receptacle located in a cavity above the micro not behind it. probably with a removable cover on the front of cabinet. Plus its an overseas item if its not listed ( I did not look into that)than the mandated instruction are kinda out the window if it violates NEC for the receptacle being accessible, so first we need to decide what NEC says about an appliance that is mounted to structure with receptacle behind it.OK so this sounds like a very long debate. How for example do you consider the outlet as per installation requirements of lets say a Miele
mircowave that"s built into a cabinet under the island. They give you a 4x 4 space in upper corner for placement of receptacle behind unit.
The appliance tech should be aware that he can shut off circuit breaker or remove unit to unplug.
any dishwasher that has a dedicated space in cabinetry and is fasten to it in my opinion. You could have one of those dishwashers on wheels that are mobile. The one with wheels would not be" built in "What exactly is a "built in dishwasher"?
Yeah I guess that what it means. I never noticed that phrase before.any dishwasher that has a dedicated space in cabinetry and is fasten to it in my opinion. You could have one of those dishwashers on wheels that are mobile. The one with wheels would not be" built in "
Here's the Sharp installation instructions. sometimes there are no place in adjacent cabinets.never seen one of those so I looked on page 44 shows the receptacle located in a cavity above the micro not behind it. probably with a removable cover on the front of cabinet. Plus its an overseas item if its not listed ( I did not look into that)than the mandated instruction are kinda out the window if it violates NEC for the receptacle being accessible, so first we need to decide what NEC says about an appliance that is mounted to structure with receptacle behind it.