Another EC sold this customer a 22kw air cooled standby generator 2/yrs ago. He called me a little over a year ago stating that every time the power went out, the generator breaker would trip.
Load calc came in at 50kw. They provided no load shedding at all. The wiring is pretty terrible as well. The lugs in the generator had no torque; I was able to pull the cables directly out of the lugs. The battery cables were the same way and completely corroded.
I sold him a 60kw, ordered in June 2022, it came in Monday this week. Removed the old generator yesterday and poured the pad for the 60kw today. I did offer to install enough load shedding devices to keep the 22kw, he insisted he wanted the whole house on at all times. He now needs a larger LP tank and fuel line as well.
I assume also this was inspected as the power company would’ve required it to re-energize the service. That inspector was fired a few months ago for letting stuff like this go.
Sent from my iPhone using Tapatalk
Load calc came in at 50kw. They provided no load shedding at all. The wiring is pretty terrible as well. The lugs in the generator had no torque; I was able to pull the cables directly out of the lugs. The battery cables were the same way and completely corroded.
I sold him a 60kw, ordered in June 2022, it came in Monday this week. Removed the old generator yesterday and poured the pad for the 60kw today. I did offer to install enough load shedding devices to keep the 22kw, he insisted he wanted the whole house on at all times. He now needs a larger LP tank and fuel line as well.
I assume also this was inspected as the power company would’ve required it to re-energize the service. That inspector was fired a few months ago for letting stuff like this go.
Sent from my iPhone using Tapatalk