Cycle timer
Smash
Can anyone recommend a single phase 240V cycle timer for a 1/4 HP motor. This is for a small chip conveyor that will be attached to a large steel cutting saw. The conveyor will simply carry the chips away from the saw into a bin. Need something for an oily industrial setting. The operator will simply turn it on and the timer will cycle for a man shift on approx 10 min then off for 30min and repeat. Or be custom programmed for that particular day of cuts. I could install an emergency stop button next to or if it came with one perfect. No variable speed no reverse just on off at programmed times. 240V Thank you for suggestions.
Did not see a hp rating. Might need to contact the manufacturer.
Ahhh, maybe not. I'll check more specs later. It might not be able to be off a different length of time than it is on. Been through this before.
What about triggering the conveyor to start up whenever the saw runs?
It would be easy to add a timer to keep it on for additional minutes if needed.
Let's start with a vibration sensor on the saw. Then for sure we know it's running instead of relying on a contactor pulling in. NEXT ... ???
I was going to count the teeth to make sure it was up to RPM then compare that with an an analog amperage input to make sure that 1/4 HP isn't overloaded on occasion.
Oooo, yeah! Use a pass through laser and high speed counter to check for any broken teeth. And get the amps off the VFD (of course). Compare that to the table in the PLC to see if the saw if getting dull. Update the maintenance schedule to bring someone in to change the blade. Use profibus and a modem to contact the tech on his iPhone.
What other solutions are looking for a problem?
Maybe just put a time off delay on it.
When the saw shuts off the chip motor will run for 10 min. Then you only need to control the saw.
Get a control volt din rail type. A set of aux on saw starter should do it. Tie into you chip saw starter/ relay
If the OP is OK with just simply running the conveyor when the saw runs a quick and easy solution would be just use a RIB current sensor with a RIB dry contact relay.