ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
In a meeting this morning, an electrician working for a PV company for whom I am doing some consulting work challenged me on my interpretation of 705, specifically about AC inverter combiner panels. They have a 600A combiner panel which has (2) 200A and (3) 80A inverter breakers along with a couple of 15A load breakers for system monitoring, and it is connected on the line side of the service disco via a 800A PV AC disco with 700A fuses. My contention is that this is a violation of 705.12(B)(3) because the combiner busbar is not qualified under any of its provisions; the applicable code is 705.12(B)(3(3) and the sum of all the breaker ratings must be less than that of the busbar. Their busbar is 600A and the total of the breaker ratings is 670A.
His contention is that since the combiner panel is interconnected on the line side of the main service disconnect, 705.12 does not apply and that it should be under 705.11, which has no provision for qualifying the busbar, so he should be able to load it up all he wants.
It went round and round after that, but I will omit the "he said, I said" and leave it at that. I am confident in my interpretation, but as I always say, I know a lot but I don't know everything. What do you think?
His contention is that since the combiner panel is interconnected on the line side of the main service disconnect, 705.12 does not apply and that it should be under 705.11, which has no provision for qualifying the busbar, so he should be able to load it up all he wants.
It went round and round after that, but I will omit the "he said, I said" and leave it at that. I am confident in my interpretation, but as I always say, I know a lot but I don't know everything. What do you think?