Transformer/Panel Wire Sizing/Conduit Fill
Electricalhelp
NJ
I received the base building drawing and was confused if the wire sizes used are correct?
For the 112.5kva transformer, shouldn't the ground on the primary be at least #6 and NOT #3 [Table 250.122]
The wire size for 350 AMP they used 4#400kcmil, #4G, 4"C
Based on my calculation, 380 AMP*.8 = 304 AMP [Table 310.16 and Current Carrying Conductors]
For 350 AMP, shouldn't the ground conductor be at least #3 and NOT #4 [Table 250.122]
The wire size for 350 AMP, I would suggest 4#600kcmil, #3G, 4"C
For the 200AMP, the wire sized they used 4#250kcmil, #6G, 2"C
Based on my calculation, 290 AMP*.8 = 232 AMP [Table 310.16 and Current Carrying Conductors]
For 232 AMP, shouldn't the ground conductor be at least #4 and NOT #6 [Table 250.122, rounded up]
Lastly if they did use 4#250kcmil, #6G, 2"C, I get a conduit fill of 47.46%, which does not meet NEC Code.
The correct wire size should be 4#4/0, #4G, 2 1/2"C or 4#250kcmil, #4G, 3"C
Let me know if any of my calculation are incorrect and if I made any mistakes as well.
See attached riser diagram for your reference
There is a lot wrong with this sketch. If building steel the GEC should be #1/0, the SSBJ to the disconnect should also be #1/0, the 400's are too small as the secondary conductors. The EGC's with the taps need to be the same size as the EGC's after the disconnect switch.
I agree with infinity that there are deficiencies in the drawing.
Note however, in your calculations you appear to be using a .8 multiplier. Unless you know a major portion of the load in non-linear (very unlikely), you don't need to count the neutral as a ccc so the .8 multiplier isn't necessary.
Do you know the size the transform,er primary OCP ??
The main breaker in the 277/480V/3 Phase Panel is 150 AMP for the transformer.
Thanks for letting me know the .8 multiplier.
So if that's the case, I should use at least 4#500kcmil, #1/0G, 4"C after the disconnect
What about the conduit for the 200AMP Panels?
Yes 500 kcmil copper (380 amps) would be the minimum size for a single set tomthe 350 amp OCPD. How long are those nipples? 24" or less and the fill jumps to 60%.
Not sure why they would specify 250 kcmil for a 200 amp panel when the conductors are 10' long. 4-#3/0 and 1-#3 EGC in a 2" conduit is what I would use.
Here is the updated riser diagram with the sizes
The EGC after the 350 amp OCPD does not need to be #1/0. Look at T250.122, for 400 amps the minimum size is #3 AWG. While we're at it what type of electrode is being used for the transformer?
But I'm still wondering how they got #3 ground wire for the transformer?
For the same reason that they got 5 other things wrong. Sounds like they used the wrong table. T250.122 would give you a #3 if you used 400 amps. The correct table is 250.66 based on the derived (secondary) conductors.
I just did a quick walk thru and now we have another issue.
Instead of a race way, they installed a 208V/600AMP/3P MCB Panel after the disconnect.
Connected the 2 Subpanels to the Distribution Panel.
I thought a 112.5 KVA transformer can have a maximum size of 400AMP?
With a 150 amp breaker on the primary the transformer is considered to be protected and the secondary does not have a limit.
The secondary conductors must be sized for 600 amp minimum
and your grounding electrode conductor must be sized accordingly
Sorry, can I ask you what code section this is so I can read about it more.
Isn't it typical for most transformers are connected with either a disconnect or a MCB on the primary side before the transformer.
So the Panel can be sized for 600AMP but the total demand load still needs to be around 400AMP only