It's outdated wherever it comes from. It's also saying the conductor to the rod can be from either the panel or the meter, not both.What is the source of that graphic?
Other than meter and panel GEC to rod, pretty similar.Other that the weirdness of showing the ground rod connected to both the meter and the service panel, that's all very normal, nothing wild. Around here we usually we have to install two rods, not just one, but don't have a meter to bond around. YMMV. But it's about right.
What is the source of that graphic?
That graphic is very misleading as it shows a connection to the gas line for the water heater which is typically not required, And it’s hard to read in all caps
Mike Holts graphics are much better
That graphic is very misleading as it shows a connection to the gas line for the water heater which is typically not required, And it’s hard to read in all caps
Mike Holts graphics are much better
Same here, and having hot-cold-gas all within about 6-8 inches of each other with no obstructions (apart from maybe a tube going to the whole-house humidifier) makes it not just "typical," but very easy to get done and out of the way.Gas piping is required to be bonded and doing it at the water heater is a very typical way for it to be done around here. AHJs look for it.
Same here. And it's even part of the annual rental housing inspection (the gas bonding)Gas piping is required to be bonded and doing it at the water heater is a very typical way for it to be done around here. AHJs look for it.
What code section requires the gas piping to bonded via an external bonding jumper?Gas piping is required to be bonded and doing it at the water heater is a very typical way for it to be done around here.
What code section requires the gas piping to bonded via an external bonding jumper?
None that I can find.What code section requires the gas piping to bonded via an external bonding jumper?
Does one prohibit the practice?None that I can find.
Nothing that I know of but I did at one time have an inspector ask for a bonding jumper to be removed on a service upgrade. He didn't like the black gas pipe on the HWH being externally bonded for some reason. I wrote a PI a few code cycles ago to clarify that it wasn't required but it got rejected.Does one prohibit the practice?
That's fine for burners, but what about oven control? Or do those use a piezo generator like water heaters?I've worked in home in the last 5 years that only had pilot-light appliances.
Thermocouple I presume? All I know is our last apartment had an old gas range with oven that didn't plug into the wall.That's fine for burners, but what about oven control? Or do those use a piezo generator like water heaters?