Just wondering what peoples' opinions, and experiences with AHJs are, on this topic.
On a residential main load center, which is the first means of disconnect, grounds and neutrals are not separated. Manufacturers typically provide neutral bar(s) which are directly connected to the neutral on the service entrance. One or more ground bars are screwed into the enclosure. A bonding screw connects the neutral bar to the enclosure, so that grounds and neutrals are connected.
Here's the question: when (if ever) is it ok to land neutrals on the ground bars ? The issue is that neutral carries ordinary service currents at full ampacity at any time, whereas ground only carries current during a ground fault (which should hopefully end quite soon). As such, there are very different requirements for size and quality of connection (e.g. ground wires can be #8 on a 100A feeder, and need be connected with only a fine-thread screw into the thin enclosure sheet metal).
This can be overcome by providing a high-current jumper from the neutral bar to any ground bar where one wishes to land neutrals. But does this violate the load center labeling/instructions ? If acceptable, how is the jumper size to be calculated ?
On a residential main load center, which is the first means of disconnect, grounds and neutrals are not separated. Manufacturers typically provide neutral bar(s) which are directly connected to the neutral on the service entrance. One or more ground bars are screwed into the enclosure. A bonding screw connects the neutral bar to the enclosure, so that grounds and neutrals are connected.
Here's the question: when (if ever) is it ok to land neutrals on the ground bars ? The issue is that neutral carries ordinary service currents at full ampacity at any time, whereas ground only carries current during a ground fault (which should hopefully end quite soon). As such, there are very different requirements for size and quality of connection (e.g. ground wires can be #8 on a 100A feeder, and need be connected with only a fine-thread screw into the thin enclosure sheet metal).
This can be overcome by providing a high-current jumper from the neutral bar to any ground bar where one wishes to land neutrals. But does this violate the load center labeling/instructions ? If acceptable, how is the jumper size to be calculated ?