400A service with (2) 200A panels
RdmanElect
Poughkeepsie NY
Electrical Contractor
I have a 400A service rated ats feeding (2) 200A panels in the basement. Just want to verify it meets code. I'm using parallel conductors
Sent from my Pixel 7 using Tapatalk
2017 NEC 312.2, last sentence: "For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations."
Cheers, Wayne
PVC connectors aren't rated for wet locations?
The connection between the connector and the enclosure is not without a sealing washer. At least one manufacturer of PVC male adapters has a sealing washer for there connectors that will give it the required rating to be installed above the live parts.
Thank you