Thanks but that for Grounded systems. How about ungrounded system over 1KV?See Art 250 Part X (part 10). 250.180 - 250.194
Yes sure,
We are using two transformers because the motor is far away, and there isn't enough room to use a large wire size due to the existing conduit constraints. The motors and Panel A operate at 480V, with the first transformer stepping up to 11KV and the second transformer stepping down from 11KV to 480V.
The first transformer is configured as 480V Y / 11KV Δ, and the second transformer is configured as 11KV Δ / 480V Y.
As you can see, the feeder between the transformers is ungrounded. Which NEC articles cover the rules we need to follow in this situation?
View attachment 2572204
The six applications covered in 240.21(C)(1) through (6)
permit transformer secondary conductors without an over-current
protective device at the point the secondary conduc-tors
receive their supply under one of the following
conditions:
1. The primary overcurrent protective device, as described
in 240.21(C)(1), can protect single-phase (2-wire) and
3-phase (delta-delta) transformer secondary conduc-tors.
what is the distance to make two transformers worth it?
Is there enough room for three 15kv cables and can you actually pull the stuff in without damage? I'd be barking up that tree before worrying about ungrounded systems. And I think if it's 11kv corner-grounded, the grounded lead can be 600v wire instead of 15kv (smaller and cheaper).there isn't enough room to use a large wire size due to the existing conduit constraints.
Yes, See 90.2 for the scope of the NEC and 250.20(C) for the requirements for AC systems over 1000V.Thank you very much, everyone. I was looking for where in the NEC rules and guidelines for ungrounded systems over 1000 volts are provided. Mostly to keep in mind for the future and for purely academic reasons. Are ungrounded systems over 1000 volts permitted in USA?
There is 110.10 which is a catch all that generally requires you can clear a fault without excessively damaging the equipment. Systems over 600V typically have to be designed and stamped by a PE around here, I don't think the regular electrical inspectors even inspect them. One of the few over 1000V I know of the customer pays the utility to have their linemen maintain it.However, it does not require the installation of ground fault detectors, which is noteworthy because it could delay the detection of initial ground faults.
Let's start there: What size is the conduit, and while I'm asking, what type, any interruptions, etc?We are using two transformers because the motor is far away, and there isn't enough room to use a large wire size due to the existing conduit constraints.
What size motor is being supplied?Because by NEC 240.21(C)
Therefore, we always use a delta configuration on the secondary side to avoid adding an 11 KV circuit breaker at the secondary. Does the NEC mention the need for a ground detector in systems over 1KV that are ungrounded?
1400 feet
You've mentioned that before is that becasue your POCO does not supply 600V service or do your irrigation suppliers not offer 600V pump panels?What size motor is being supplied?
For irrigation wells around here we run into similar distance on most installations and run up to 125 HP motors all the time with up to around 2000 feet of 480 volt supply conductors.
Center pivot irrigation machines are all 480 volt, never seen one that was any other voltage. Well pump motors are only stocked in 480 volt. For whatever reason that is what they started out with long ago and it likely not going to change now with so many out there that are 480 volts. Under 75 HP you do find them as 230/460 dual volts but 75 and up is almost always single voltage 460, may have leads for part winding start or wye/delta start though nobody uses that anymore. POCO's usually only require reduced voltage starting on motors over 100 HP but most those anymore are done with soft starters.You've mentioned that before is that becasue your POCO does not supply 600V service or do your irrigation suppliers not offer 600V pump panels?
Since no one has come out and said it, No you do not need to ground MV systems, and you do not even need ground detectors.Thanks.
Article 250.20(C) addresses ungrounded systems above 1000 volts, permitting them provided they do not supply mobile or portable equipment. However, it does not require the installation of ground fault detectors, which is noteworthy because it could delay the detection of initial ground faults.
On the other hand, according to 250.21(B), ungrounded AC systems allowed under 250.21(A)(1) through (A)(4), operating between 120 volts and 1000 volts, must have ground fault detectors installed. However, there is no such requirement specified for systems operating above 1000 volts.