220.57 Electric Vehicle Supply Equipment (EVSE) Load.
The EVSE load shall be calculated at either 7200 watts (volt-amperes) or the nameplate rating of the equipment, whichever is larger.
625.42 Rating.
The EVSE shall have sufficient rating to supply the load served. Electric vehicle charging loads shall be considered to be continuous loads for the purposes of this article. Service and feeder shall be sized in accordance with the product ratings, unless the overall rating of the installation can be limited through controls as permitted by
625.42(A) or (B).
220.53 Appliance Load — Dwelling Unit(s).
Applying a demand factor of 75 percent to the nameplate rating load of four or more appliances rated 1⁄4 hp or greater, or 500 watts or greater, that are fastened in place, and that are served by the same feeder or service in a one-family, two-family, or multifamily dwelling shall be permitted. This
demand factor shall not apply to the following:
(5)Electric vehicle supply equipment (EVSE)