As currently worded in NEC, various ambient temperatures may quailfy to be used in either table because ambient temperatures may be simultaniously other than 30 degrees celcius table 310.15B11 and or other than 40 degrees celcius table 310.15 B12
Therefore, the NEC is not clear on which to use.
For example:
A mid point ambient temperature between 30 and 40 degrees celcius could be 35 degrees celcius
An ambient temperature of 35 degrees celcius is both "other than 30 degrees celcius" table 310.15B11 and is also "other than 40 degrees celcius"
Therefore, which table does NEC expect the electrician to use for ambient temperature correction factors and wire ampacity determination based on their wording?
I do understand that the second table includes higher ambient temperatures but this still does answer which table to use according to the info within table titles
following is an example by the 2023 NEC handbook. Notice that the answer is based on a 90 degree THHN copper conductor insulation which we know cannot terminate on most utilization equipment typically rated for 75 degrees maximum
2) NEC hand book example
Determine the ampacity of 2 AWG THHN copper conductors to be installed in a raceway in an ambient temperature of 50 degrees celcius
NEC Answer
Table 310.16
Start at 130 ampere THHN at 90 degree insulation
Next NEC chose table 310.15B111, instead of table 310.15B12?
130i x 0.82 (derating factor based on 90 degree insulation) = 106.6 amperes
However if not simply terminating to a connector, bus or power block rated for 90 degrees celcius, should the ampacity of the wire be reduced to its maximum current value of 115 amperes (table 310.16) for a 75 degree utilization device termination point?
Also if the second table 310.15B12 were used instead we would have had an original wire ampacity of 130i x 0.89 = 115.7 amperes but NOT the 106.6 amperes shown by the NEC hand book as an answer.
Thanks
Therefore, the NEC is not clear on which to use.
For example:
A mid point ambient temperature between 30 and 40 degrees celcius could be 35 degrees celcius
An ambient temperature of 35 degrees celcius is both "other than 30 degrees celcius" table 310.15B11 and is also "other than 40 degrees celcius"
Therefore, which table does NEC expect the electrician to use for ambient temperature correction factors and wire ampacity determination based on their wording?
I do understand that the second table includes higher ambient temperatures but this still does answer which table to use according to the info within table titles
following is an example by the 2023 NEC handbook. Notice that the answer is based on a 90 degree THHN copper conductor insulation which we know cannot terminate on most utilization equipment typically rated for 75 degrees maximum
2) NEC hand book example
Determine the ampacity of 2 AWG THHN copper conductors to be installed in a raceway in an ambient temperature of 50 degrees celcius
NEC Answer
Table 310.16
Start at 130 ampere THHN at 90 degree insulation
Next NEC chose table 310.15B111, instead of table 310.15B12?
130i x 0.82 (derating factor based on 90 degree insulation) = 106.6 amperes
However if not simply terminating to a connector, bus or power block rated for 90 degrees celcius, should the ampacity of the wire be reduced to its maximum current value of 115 amperes (table 310.16) for a 75 degree utilization device termination point?
Also if the second table 310.15B12 were used instead we would have had an original wire ampacity of 130i x 0.89 = 115.7 amperes but NOT the 106.6 amperes shown by the NEC hand book as an answer.
Thanks