ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
Scenario:
A client requested assistance from a consulting engineer on a project connecting 480/277V inverters to a 208/120V service. The engineer recommended using a 208V delta to 480/277V wye transformer. The client instead bought and installed a 208/120V wye to 480V delta transformer. The client is lucky because he is using SE inverters which can connect to a 480V delta service, and he does not want to replace the (large, expensive, and probably not returnable) transformer with the recommended one.
The client installed the transformer with the neutral connected back to the service from the transformer primary. The engineer advised the client to remove the neutral connection to the service, making the transformer essentially delta-delta. The client did so, but in the process the engineer saw that the client had also bonded the transformer primary neutral to ground, connecting the neutral and ground conductors between the service and the transformer in parallel, which is a clear code violation.
The question:
The client has removed the neutral connection between the service and the transformer primary, but the otherwise floating primary neutral is still connected to ground; is this a problem?
Aside:
The system was inspected and green tagged by the POCO, despite that the transformer is not the same as the one on the sealed planset, there are numerous discrepancies in wiring, and the code violation.
A client requested assistance from a consulting engineer on a project connecting 480/277V inverters to a 208/120V service. The engineer recommended using a 208V delta to 480/277V wye transformer. The client instead bought and installed a 208/120V wye to 480V delta transformer. The client is lucky because he is using SE inverters which can connect to a 480V delta service, and he does not want to replace the (large, expensive, and probably not returnable) transformer with the recommended one.
The client installed the transformer with the neutral connected back to the service from the transformer primary. The engineer advised the client to remove the neutral connection to the service, making the transformer essentially delta-delta. The client did so, but in the process the engineer saw that the client had also bonded the transformer primary neutral to ground, connecting the neutral and ground conductors between the service and the transformer in parallel, which is a clear code violation.
The question:
The client has removed the neutral connection between the service and the transformer primary, but the otherwise floating primary neutral is still connected to ground; is this a problem?
Aside:
The system was inspected and green tagged by the POCO, despite that the transformer is not the same as the one on the sealed planset, there are numerous discrepancies in wiring, and the code violation.