A 15A branch circuit is being upsized to 12/2 romex for a long run (130'). Can you pull the homerun in 12/2 romex and have jumpers to other receptacles downstream be in 14/2 Romex?
Question is from a Code standpoint to begin with. But also from an electrical theory standpoint.
The voltage dropped is across the whole circuit (someone could potentially pull 12A off that 15A circuit at the last receptacle. Would this cause an issue to say, the 10' jumper from box containing the HR (with 12/2 HR) to next receptacle (14/2 from HR box onward).
Bonus Question - If you do a voltage drop calculation on this (2x12.9x130'x12A = 40240/3.6V(3% VD on 120V circuit) = 11,180cm) (#10 = 10380cm). This leads me to believe, to properly stay below 3% Vd, you should run 8/2 NM to these receptacles. Is this "Correct" and are people doing this?
What am I missing/ not understanding?
Question is from a Code standpoint to begin with. But also from an electrical theory standpoint.
The voltage dropped is across the whole circuit (someone could potentially pull 12A off that 15A circuit at the last receptacle. Would this cause an issue to say, the 10' jumper from box containing the HR (with 12/2 HR) to next receptacle (14/2 from HR box onward).
Bonus Question - If you do a voltage drop calculation on this (2x12.9x130'x12A = 40240/3.6V(3% VD on 120V circuit) = 11,180cm) (#10 = 10380cm). This leads me to believe, to properly stay below 3% Vd, you should run 8/2 NM to these receptacles. Is this "Correct" and are people doing this?
What am I missing/ not understanding?