NEC 310.15 E provides 3 scenarios where a neutral is to be considered current carrying. This is especially useful for adjusting a conductors ampacity when bundled such as in conduit with more than 3 current carrying conductors.
The code says:
1) a neutral that carrys only the unballace current from the same circuit is NOT counted
2) in a 3 phase, 4 wire WYE system, the neutral is counted
3) in a 3 phase, 4 wire WYE system, serving nonlinear loads, the neutral is counted
HOWEVER NEC code point 3) DOES NOT NEED TO BE HERE BECAUSE NEC ALREADY SAID ALL 4 WIRE Y SYSTEMS WITH A NEUTRAL ARE TO HAVE NEUTRALS COUNTED REGARDLESS OF LOAD TYPE
Second, why do we not see single or "split phase" systems included here. A single phase 2 wire with ground circuit (other than a multi-wire branch circuit) can be shown with a clamp on ammeter to have equal current in the grounded neutral as compared to the ungrounded wire
If for example, wires are ran in a conduit for two 120V receptacles supplied from a single phase system (1 hot and 1 neutral per receptacle) , why is NEC not listing this as a neutral to be counted as current carrying. (Excluding MWBC)?
The code says:
1) a neutral that carrys only the unballace current from the same circuit is NOT counted
2) in a 3 phase, 4 wire WYE system, the neutral is counted
3) in a 3 phase, 4 wire WYE system, serving nonlinear loads, the neutral is counted
HOWEVER NEC code point 3) DOES NOT NEED TO BE HERE BECAUSE NEC ALREADY SAID ALL 4 WIRE Y SYSTEMS WITH A NEUTRAL ARE TO HAVE NEUTRALS COUNTED REGARDLESS OF LOAD TYPE
Second, why do we not see single or "split phase" systems included here. A single phase 2 wire with ground circuit (other than a multi-wire branch circuit) can be shown with a clamp on ammeter to have equal current in the grounded neutral as compared to the ungrounded wire
If for example, wires are ran in a conduit for two 120V receptacles supplied from a single phase system (1 hot and 1 neutral per receptacle) , why is NEC not listing this as a neutral to be counted as current carrying. (Excluding MWBC)?