Jimmy7
Senior Member
- Location
- Boston, MA
- Occupation
- Electrician
I have a customer who wants some recessed lights replaced. Someone dropped the housings to refinish the wood ceiling and the housings got destroyed. In any case the housings are 5” shallow housings. I wasn’t going to install wafer lights because one fixture has three cables going to it, and I thought the wafer lights junction box would be too small. There are three lights, but one has two 14-2, and one 14-3 going to it (Drawing attached). I did not see a cubic inch on the junction box, so I measured the inside dimensions of the housing’s junction box which were 1.5 x 2.5 x 3.75 =14.0625. Two 14-2 and One 14-3 have wire fill of 16 cu in. Am I looking at this right? If so, what is the best way out of this? The owner wouldn’t want me cutting a junction box into the ceiling..