I’m trying understand 110.14 (C).
“C) Temperature Limitations. The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.”
So applicability wise, when sizing a conductor, you start with the ampacity specified in table 310.16. Then, if needed, derate for temperature and current carrying conductors amount. Then, if under 800 A, you can upsize your breaker to the nearest standard size per 240.4(b).
My question. Is 110.14(c) saying your final adjusted ampacity can not exceed the 60°C or 75°C ampacity in table 310.16?
“C) Temperature Limitations. The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.”