running 480v machine on 380v
Emad
Libya
Electrical engineer
hi
we have miller proheat 35 (heat treatment machine 35kw) that designed for 460/575v power supply.but the site power supply is 380v.
A step up transformer with this ratio is not avaivlbe in the market. what are other options we have ?
He would need to check with Miller on his specific model and frequency, but on the looks of it, I doubt it.
Thanks everybody
I please review the machine nameplate attached
Probably could be run at 380-400 native voltage with a higher amperage, but would need to get miller's blessing with his model and frequency specifics.
The cut sheet specifications shown above show 400-460V @50/60Hz, only the input amps required varies for the voltage supplied.
The model tag shows 460-575V at both 50/60Hz I doubt that there would be a different model for 380V, likely it would just need a bit more current, the spec sheet shows 60A current @400V, you would be wise to ask Miller directly if the machine can be operated at 380V 50 Hz directly, and avoid the use of a transformer.
I have one of their older model Inverter welding power units and it will operate off of three different voltages as well as single and three phase, without changing any wiring input configurations. My guess is that this inverter heating power supply is designed very similarly. You could look in your manual, it may spell it out in there, as the nameplate tag has limited room for information.
In an inverter machine, most of the AC current is rectified into DC and then inverted into high frequency, and your nameplate implies that, but again it would be wise to check the manual or ask Miller directly, instead of making assumptions or taking my suggestions.
To be on the safe side, I recommend asking them directly or looking in the manual shipped with the unit. But I would doubt that you need the transformer as long as you provide it enough current for full output, if required.
In the American market 380-415V 50Hz is considered the universal European voltage and most things will operate fine if supplied within that range. Have you actually measured your voltage at the site where the heater will be operated, instead of just taking someones word for the standard voltage in the area?
Thank you MTW for you kind clarification.
For manual,miller seems to have two unit ranges.
OK I will try to email them.
  • Like
Reactions: MTW
Assuming the native voltage won't work, you just have to get within the range. A 1.5:1 transformer would work. Or a 2:1 with a small buck.
hi
A 480 Delta to 380Y is readily available, what about using it in reverse? Just make sure the XO floats with no supply neutral connected.
I agree there is not likely a different power design. The unit nameplate only shows a CSA label on it, so it was likely intended only for sale in Canada, so they didn’t bother showing voltages that are not available there. For 400V use in IEC countries they have to add a filter, often called a “CE filter” to be able to pass more stringent electrical noise standards in the EU. If that were added to units being sold only for use in the US or Canada, that filter would have to be tested by UL and CSA. So they leave it off for domestic (to N. America) use.
But if Lybia follows the same standards as the EU and you cannot connect it to the grid without a CE sticker, you are going to need that filter.
Thank you Indeed that was very helpful and logical
Thanks a million
