480v high leg motor issue
journeyman0217
Tennessee
i am troubleshooting a three phase 480 motor with voltage issues that is fed by a high leg system. I dont have to much experience with this set up. Would the configuration of the connections to the motor matter? It is fed by a 3 wire 480v delta high leg system. i did not think it would matter because it is a 3 phase motor, not single phase.
It’s a step up transformer. Service coming in is 240v three phase high leg. Steps it up to feed the motor.
I'm trying to understand it...wouldn't the secondary induced voltage have the same effect as the primary? Wouldnt my voltage on the 480 side be (L1-G 240, L2-G 416, L3-G240)?
Only if the center of the L1-L3 winding was bonded to “ground.” Does the winding even have a center tap?
OP, That is a Delta to Delta transformer. You would need to bond the secondary at some point to get a reliable reference voltage to ground.
I don't think that transformer is being used correctly if it is step-up as you suggest. It may not have anything to do with your problem though.
No center tap.
It is a delta-delta transformer and has no center tap according to posted nameplate. there are voltage adjustment taps on the high voltage side. If OP is having low voltage issues the tap being used could possibly come into play. Being reverse fed situation he probably should use one of the mid range taps though.