electric man 31
Member
- Location
- Connecticut
please help with a service calculation i have!! The building in question is a dog kennel it has 3 phase power 120/208 volt service rated @ 200 amps. The highest kw reading from the power co. was 61.5 kw, I feel that his service is about maxed out becouse @ 80% the service should be good for 57 kw. Do you feel the same way ?, if so how do I relay the information correctly to the customer maybe my calculation is off and I dont need to sell him a service upgrade to a 400 amp service,however I feel he has no room for any extra equiptment down the road electricman31@aol.com