I went to a friend of a friend's place today to install a ceiling fan in the baby's bedroom. The only switch in the room controlled half of a duplex receptacle, so I had to put in a new ceiling outlet for the fan. My idea was to make the switched receptacle unswitched, yank out the existing switch, put in a single-gang dual dimmer to control the light and fan, and run some 14/3 NM from the dual dimmers to the new outlet. I did all this, and everything worked according to plan. Homeowner and wife were pleased.
So all that was left was to swap out the existing breaker and put in an AFCI. Guess what I found inside the panel. Yep -- the circuit in question was half of a multiwire circuit. The only AFCIs I've installed previously were on circuits I installed myself, and I only use multiwire circuits in very limited instances (e.g., dishwasher/disposal receptacle). It never occurred to me that the AFCI wouldn't work on a multiwire circuit, but it sure didn't. It was also the first statement in the instructions that came with it.
So the problem is that the ceiling fan works fine as long as I leave the old breaker in place, which is not code-compliant. Just about every cable leaving the panel is a multiwire circuit, and the few that aren't are nowhere near where I could tap into them and/or are illegal for me to tap into.
The house is a three-level 3000 sq. ft townhouse built in 1989, totally finished everywhere except the small furnace/panelboard room on the lower level, and the bedroom I worked on is on the upper level, nowhere near the panel.
Anyone have any brilliant ideas as to how I can keep the new ceiling fan working and be code-compliant at the same time? Running a new circuit for this new outlet would be a seriously major PITA.
So all that was left was to swap out the existing breaker and put in an AFCI. Guess what I found inside the panel. Yep -- the circuit in question was half of a multiwire circuit. The only AFCIs I've installed previously were on circuits I installed myself, and I only use multiwire circuits in very limited instances (e.g., dishwasher/disposal receptacle). It never occurred to me that the AFCI wouldn't work on a multiwire circuit, but it sure didn't. It was also the first statement in the instructions that came with it.
So the problem is that the ceiling fan works fine as long as I leave the old breaker in place, which is not code-compliant. Just about every cable leaving the panel is a multiwire circuit, and the few that aren't are nowhere near where I could tap into them and/or are illegal for me to tap into.
The house is a three-level 3000 sq. ft townhouse built in 1989, totally finished everywhere except the small furnace/panelboard room on the lower level, and the bedroom I worked on is on the upper level, nowhere near the panel.
Anyone have any brilliant ideas as to how I can keep the new ceiling fan working and be code-compliant at the same time? Running a new circuit for this new outlet would be a seriously major PITA.