I just hate it when I discover that I may have been doing something wrong for years...
Article 501.5(F)(3) discusses drain and sealing requirements for Canned Pumps, Process or Service Connections.
1. What is a canned pump?
2. By process or service connections are we talking about all those electrical switches and transmitters that connect to, and measure, the process conditions in a plant? All the temperature, level, flow, and pressure devices?
Let's say we have an explosionproof pressure switch that connects to a vessel and measures pressure at 600 psig.
Inside the explosionproof junction box is a bourdon tube that is connected through mechanical linkage to a microswitch. The bourdon tube provides a primary seal to isolate the process pressure from the electrical system. The electrical conduit connected to this explosionproof junction box is sealed to maintain the explosionproof integrity of the box, but it is not designed to withstand a continuous pressure across the seal. So if the primary seal fails, the process fluid could enter the electrical conduit.
In this case an additional "approved" seal is required and a means of draining the fluid needs to be provided as a visual indication that the primary seal has failed. Am I reading this correctly? API RP 14F takes this a step further and requires that the drain be capable of reducing the "fluid pressure under dynamic conditions to less than 6 inches of water column upon failure of primary seal." ... That would be some drain!
3. I have never seen a field device (switch or transmitter) labeled with the number of seals it has internally. Would this be part of the listing requirements? And if it is not listed or labeled how can I determine if it meets the requirement of Article 501.5(F)(3)?
4. What is this additional "approved seal, barrier, or other means" which can be used? I have never seen one installed and I have never seen one in any trade literature.
Or am I reading this whole section wrong?
Any help would be appreciated.
Article 501.5(F)(3) discusses drain and sealing requirements for Canned Pumps, Process or Service Connections.
1. What is a canned pump?
2. By process or service connections are we talking about all those electrical switches and transmitters that connect to, and measure, the process conditions in a plant? All the temperature, level, flow, and pressure devices?
Let's say we have an explosionproof pressure switch that connects to a vessel and measures pressure at 600 psig.
Inside the explosionproof junction box is a bourdon tube that is connected through mechanical linkage to a microswitch. The bourdon tube provides a primary seal to isolate the process pressure from the electrical system. The electrical conduit connected to this explosionproof junction box is sealed to maintain the explosionproof integrity of the box, but it is not designed to withstand a continuous pressure across the seal. So if the primary seal fails, the process fluid could enter the electrical conduit.
In this case an additional "approved" seal is required and a means of draining the fluid needs to be provided as a visual indication that the primary seal has failed. Am I reading this correctly? API RP 14F takes this a step further and requires that the drain be capable of reducing the "fluid pressure under dynamic conditions to less than 6 inches of water column upon failure of primary seal." ... That would be some drain!
3. I have never seen a field device (switch or transmitter) labeled with the number of seals it has internally. Would this be part of the listing requirements? And if it is not listed or labeled how can I determine if it meets the requirement of Article 501.5(F)(3)?
4. What is this additional "approved seal, barrier, or other means" which can be used? I have never seen one installed and I have never seen one in any trade literature.
Or am I reading this whole section wrong?