Re: Ground to Neutral voltage
In a correctly installed system the grounded (neutral) to grounding conductor voltage is a measurement of the voltage drop on the grounded conductor between the main bonding jumper and the point where the voltage is being measured. Since one half of the circuit voltage drop is on the grounded conductor, the 2 volt neutral to grounding conductor voltage represents a 3.3% voltage drop on that circuit (assuming a 120 volt circuit).
Don
[ August 20, 2003, 03:36 PM: Message edited by: don_resqcapt19 ]