Romex

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You can use 90deg for derating and when 90deg terminations are required but in the end you have to protect it as a 60deg conductor
(see 334.80)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I should have explained myself better (story of my life).. I was thinking about items that require 90deg rated conductors such as some light fixtures
 
Top