Seal off in a junction box

Mr. Pickle

Member
Location
Rogers MN
Occupation
Electrical
Have a client who would like to explore an in-grade junction box option.

If we have a conduit coming from a class 1, div. 2, group D location, running underground to a junction box. Can we put the seal-off inside the in-grade junction box?

Thinking of using the attached junction box for the in-grade junction box in this case. NEMA 7 not because of its hazardous location rating, but rather because it is water tight.
 

Attachments

  • Pages from crouse-hinds-ecp-brochure (002).pdf
    421.7 KB · Views: 9

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
If we have a conduit coming from a class 1, div. 2, group D location, running underground to a junction box. Can we put the seal-off inside the in-grade junction box?
That isn't a recognized Section 501.15 sealing method.
Thinking of using the attached junction box for the in-grade junction box in this case. NEMA 7 not because of its hazardous location rating, but rather because it is water tight.
Actually, below grade, it probably puts it in a Division 1 location as well. where sealing is per 501.15(A).
 