Selecting a surge protector for

sunny1

Member
Location
Washington State
Occupation
electrician
I would like to add surge protection to a Square D I-line panelboard at one of our facilities and I am confused about the MCOV rating of the surge protector below. It is a 3phase 120/240 service with a 208v high leg, so I believe this is the right one, but I don't understand how the MCOV is 150v. The L-G voltage of the service has to be lower than the MCOV of the SPD, so how would this work with the high leg? I used the picture below for this post, but it says the same thing in the square d catalog.

Thanks ahead of time.
1714434574176.png
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
In the product details, it shows H, L, N, and G; apparently, H refers to the high-leg line.

The 150v rating should probably have another, higher number next to it.
 

sunny1

Member
Location
Washington State
Occupation
electrician
In the product details, it shows H, L, N, and G; apparently, H refers to the high-leg line.

The 150v rating should probably have another, higher number next to it.
Thanks for the response, that's what I thought too. Just wasn't sure if I was missing something. I will see if my supplier can clarify as that is the only MCOV rating on the data sheet that I could find. 120/240 high leg delta indicates a three phase service with 120v on two phases and 208 on the high leg, with 240v L-L unless there is another configuration I am unaware of?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I will see if my supplier can clarify as that is the only MCOV rating on the data sheet that I could find. 120/240 high leg delta indicates a three phase service with 120v on two phases and 208 on the high leg, with 240v L-L unless there is another configuration I am unaware of?
What is the MCOV for a 208Y unit?

They probably combine two 120v and one 208v device.
 

sunny1

Member
Location
Washington State
Occupation
electrician
Looks like it is also 150 v on the 208y. I must be overthinking this, it's the device designed for the service I have, I just wanted to triple check because they are very expensive. I was thinking about it and if the MCOV was like 230v or something that wouldn't be good either because I wouldn't be protecting the 120v phases until the surge surpassed 230v correct? Thanks again for the response.
 