Temporary job site power

nizak

Senior Member
I usually set a “skid” with a 6 space MLO panel and a couple of 20amp circuits with two GFCI receptacles for job site power.

It feeds from a source with a 2 pole breaker and 4 wire SO cord.

Inspector said I need a service disconnect for the temp.

Can that be a breaker retaining clip on the 2 pole breaker feeding the skid at the source or does it need to be in the skid panel itself?

First time I’ve encountered this
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You can use a back-fed breaker as the single service disconnect with requisite screw or clip.
 