crazymanmark7584
Member
- Location
- Poughkeepsie, NY
We were called to a local fitness gym that has a very old electrical distribution system. There's a lot of old crap in there, but we have a problem with one of the newer panels that feeds treadmills.
The call was that there was 8 machines about a year ago that had the circuit boards blow up. They were subsequently replaced under warranty of the machine manufacturer.
Then about 3 months ago, a large storm came through the area, and a similar problem occurred, this time with 7 circuit boards in the treadmills "blowing up".
Long long story short, the owner seemed to remember that other panels in the building were balanced, eliminating the problem. It kind of makes sense, sort of, in that balancing the loads would make for a cleaner neutral, potentially eliminating any strange spikes or faults on the phases.
The maintenance tech for the building told me before arriving on site that balancing the loads would potentially work, and to try it, and to look for anything else we could find. So, we investigated. Once opening the panel it was realized it was a single phase 200 amp Main lug only panel. Amp prope on the legs showed about 9 amps on one leg and 11 on the other. It was hard to balance this, 1. because it was pretty close to begin with, and 2. people rotate in and out on the machines constantly
Beyond this, the panel is fed separately metered on the outside of the building. The building is old as I mentioned, and instead of tapping this panel from somewhere, they installed a new meter and riser. On the back of the building this meter is located along with an exterior 200 amp main breaker enclosure.
At this breaker, the installer pulled 3x4/0 aluminum feeders and one #4 bare ground through a 2" EMT, through the space to this panel at the front of the building. It is about 150 linear feet total.
There is another #4 bare copper ground from the neutral lug in the breaker enclosure to a ground rod directly underneath the meter and breaker. I did not measure the resistance on the rod. Upon further review, the ground wire was broken to this rod, as it appears it was broken by a lawn mower or weed whacker. We re-spliced it and continued investigating.
The rest of the building is fed with a 3 phase high leg system, with multiple CT meters both inside and out on the pole (3 total). We did not look for building steel and/or cold water bonds on any of the existing distribution equipment. (this includes 3x 400amp 3 phase disconnects and 1 400 amp CT cabinet, among many other things. It is such a mess I could spend hours figuring where it all goes and still not be totally sure what I'm looking at.)
So, the point...Is this existing 200 amp MLO "sub-panel", that is breaker-ed at the back of the building, about 150 feet away, required to be bonded to building steel? Or is the service that feeds it, for that matter? Like I said, it was grounded to a ground rod at the location of the breaker. This panel IS wired like a sub panel, as in grounds and neutrals are separate.
Secondly, if it is required to be bonded to building steel (which I think it should be....), WHERE should/can this bond be located? At the panel 150' away, or should it be as close to this exterior breaker as it can be?
Is a second ground rod advisable, or allowed per NEC, or is it necessary?
I am being told by other electricians this service needs to be bonded to allow for a backup grounded conductor, should the utility neutral fail, OR should the ground rod/conductor fail, which it did since it was broken.
I went ahead and got a piece of #4 bare copper and bonded the neutral bar to building steel at the problem panel. Is this right, wrong, unnecessary, or just plain dumb?
Advice, please!
Thank you in advance.
-Mark
The call was that there was 8 machines about a year ago that had the circuit boards blow up. They were subsequently replaced under warranty of the machine manufacturer.
Then about 3 months ago, a large storm came through the area, and a similar problem occurred, this time with 7 circuit boards in the treadmills "blowing up".
Long long story short, the owner seemed to remember that other panels in the building were balanced, eliminating the problem. It kind of makes sense, sort of, in that balancing the loads would make for a cleaner neutral, potentially eliminating any strange spikes or faults on the phases.
The maintenance tech for the building told me before arriving on site that balancing the loads would potentially work, and to try it, and to look for anything else we could find. So, we investigated. Once opening the panel it was realized it was a single phase 200 amp Main lug only panel. Amp prope on the legs showed about 9 amps on one leg and 11 on the other. It was hard to balance this, 1. because it was pretty close to begin with, and 2. people rotate in and out on the machines constantly
Beyond this, the panel is fed separately metered on the outside of the building. The building is old as I mentioned, and instead of tapping this panel from somewhere, they installed a new meter and riser. On the back of the building this meter is located along with an exterior 200 amp main breaker enclosure.
At this breaker, the installer pulled 3x4/0 aluminum feeders and one #4 bare ground through a 2" EMT, through the space to this panel at the front of the building. It is about 150 linear feet total.
There is another #4 bare copper ground from the neutral lug in the breaker enclosure to a ground rod directly underneath the meter and breaker. I did not measure the resistance on the rod. Upon further review, the ground wire was broken to this rod, as it appears it was broken by a lawn mower or weed whacker. We re-spliced it and continued investigating.
The rest of the building is fed with a 3 phase high leg system, with multiple CT meters both inside and out on the pole (3 total). We did not look for building steel and/or cold water bonds on any of the existing distribution equipment. (this includes 3x 400amp 3 phase disconnects and 1 400 amp CT cabinet, among many other things. It is such a mess I could spend hours figuring where it all goes and still not be totally sure what I'm looking at.)
So, the point...Is this existing 200 amp MLO "sub-panel", that is breaker-ed at the back of the building, about 150 feet away, required to be bonded to building steel? Or is the service that feeds it, for that matter? Like I said, it was grounded to a ground rod at the location of the breaker. This panel IS wired like a sub panel, as in grounds and neutrals are separate.
Secondly, if it is required to be bonded to building steel (which I think it should be....), WHERE should/can this bond be located? At the panel 150' away, or should it be as close to this exterior breaker as it can be?
Is a second ground rod advisable, or allowed per NEC, or is it necessary?
I am being told by other electricians this service needs to be bonded to allow for a backup grounded conductor, should the utility neutral fail, OR should the ground rod/conductor fail, which it did since it was broken.
I went ahead and got a piece of #4 bare copper and bonded the neutral bar to building steel at the problem panel. Is this right, wrong, unnecessary, or just plain dumb?
Advice, please!
Thank you in advance.
-Mark