NEC Codes or IEEE Standards?

Status
Not open for further replies.

burchie

Member
Location
Jackson, SC
Hello,
I would like to ask if there are any NEC Codes or IEEE Standards for bonding a shield on a 120 VAC power circuit from a power panel through raceway/cable tray to a control panel?
Thank you for your input on this topic.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I take it the shield isn't needed? or are you asking if the control panel needs to be bonded with the shield?
 
Hello,
I would like to ask if there are any NEC Codes or IEEE Standards for bonding a shield on a 120 VAC power circuit from a power panel through raceway/cable tray to a control panel?
Thank you for your input on this topic.
  • What purpose the shield on a 120VAC power wire serves?
  • What kind of shield?
  • If it is a metallic 'shield' that can become energized due to insulation failure on the wires within, then it is indeed need to be bonded.
 

burchie

Member
Location
Jackson, SC
Reply: NEC Codes or IEEE Standards

Reply: NEC Codes or IEEE Standards

It is a braided shield and it is not needed, but we were given this cable to use and just wanted to know whether to bond the shield at one end, both ends or not at all.
And is there some code or standard reference to that effect


Thank you
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Well if it is possible for the wire to get energized in the cable due to a fault then I believe it needs to be connected to clear any faults. IMO, one end is all that is necessary to bond it.
 