For some reason the height requirement of 28 inches with a horizontal distance of 30 inches of perimeter surfaces keeps getting inserted as an exception to exempt the bonding grid.
IMO, CMP 17 has accepted reasoning by the hot-tub industry that at 28 inches horizontal above ground, there will not be a chance that a person can have 1 foot in the tub at the same time the other is on the (possibly stray voltage energized) perimeter surface as they enter the tub, therefore no one will get hurt.
Think about it, if a permanently installed above ground pool is installed, it requires the perimeter bond, so why not apply the same principal to a hot-tub? The hot-tub industry also argued that a hot-tub should be considered as portable. The only time I?ve seen a hot-tub being portable is when it is installed or removed from the property.
Under pressure from the hot-tub industry and no body count directly related to hot-tubs, CMP 17 passed TIA 11-1
IMO, the same documented evidence of stray voltage hazards that implemented the perimeter bond for permanently installed pools can be used as guidance for perimeter bonding to be applied to hot-tubs.
shortcircuit