Is it acceptable to bond steel sealtight connectors according to OSHPD?

Is this what you are looking for?
350.60 Grounding and Bonding. If used to connect equipment where flexibility is necessary to minimize the transmission of vibration from equipment or to provide flexibility for equipment that requires movement after installation, an equipment grounding conductor shall be installed.
Where flexibility is not required after installation, LFMC shall be permitted to be used as an equipment grounding conductor when installed in accordance with 250.118(6).
Where required or installed, equipment grounding conductors shall be installed in accordance with 250.134(B).
Where required or installed, equipment bonding jumpers shall be installed in accordance with 250.102.
 