service entrance conductors to a single Dwelling

Status
Not open for further replies.

JAJ

New member
Location
Watford City ND
In rural enviroments where I'm from it's common to see the metersocket and disconnect switch located outside of the dwelling. At the metersocket the utility company usually drives a ground rod and bonds the neutral conductor. My question pertains to the service entrance conductors going from Disconnect to inside the house. Would I need to run a grounding conductor to my panel as well? What I think is right is, if I have a main disconnect outside that is bonded you would be required to run a grounding conductor and of course not bond in your house panel. I've seen it done so many ways with and without using a grounding conductor that i've lost track. thanks
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
You are correct, after the Main all wiring downstream needs an Equipment Grounding Conductor.

Roger
 