Connection of Grounding Electrode Conductor in 810.51.F

Status
Not open for further replies.

LPA

Member
Location
Dayton, OH, USA
If an Antenna Discharge Unit (ADU) is positioned in close proximity to building steel, which is in turn a member of the Grounding Electrode System (GES), must it's Grounding Electrode Conductor (GEC) bypass termination with the building steel in favor of being routed all the way back to the building's Intersystem Bonding Termination (IBT)?

It would seem that the impedance of the building steel would be much lower than that of the GEC and would better perform the intended function.
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
Just install a #6 CU jumper from the building steel to the antenna. No need to run all the way back to the service equipment.
 