Eco Smart Tankless Water Heater requires two EGCs

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
An Eco Smart Tankless water heater is installed with two or three 40 amp circuits. Two for the smaller unit and three for the larger. The installation instructions specify a separate EGC for each circuit. I saw an installation video on YouTube where the installer used EMT from the panel to the heater. Two 40 amp circuits with two EGCs. Any idea why a ground for each circuit it required?

http://https://www.youtube.com/watch?v=Okzydipeno0
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
An Eco Smart Tankless water heater is installed with two or three 40 amp circuits. Two for the smaller unit and three for the larger. The installation instructions specify a separate EGC for each circuit. I saw an installation video on YouTube where the installer used EMT from the panel to the heater. Two 40 amp circuits with two EGCs. Any idea why a ground for each circuit it required?

http://https://www.youtube.com/watch?v=Okzydipeno0


probably because that will always work and meet code. most of these things get installed by plumbers and they want to try and make sure the worst case is covered would be my guess.

suppose you run both circuits in the same PVC conduit. by code, you only need run a single EGC.

but if you ran them in separate PVC conduits, you need to run an EGC in each conduit.

it may also be something that was left over from some European instructions.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Before I watched the video, I would have guessed the components of the heaters were isolated from one another, thus requiring two or three grounds. After watching, idk. mfg specs.
 