GROUNDING A WELDING SHELTER

Status
Not open for further replies.

rose1981

Member
Location
TX
I wonder if I should ground a welding shelter. The shelter is like a roofed structure on four columns. It doesn't have any walls. In the center of the shelter is the welding receptacles mounted on a unistrut.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Yes,
250.32 Buildings or Structures Supplied by a
Feeder(s) or Branch Circuit(s)
(A) Grounding Electrode. Building(s) or structure(s) sup-
plied by feeder(s) or branch circuit(s) shall have a grounding
electrode or grounding electrode system installed in accor-
dance with Part III of Article 250. The grounding electrode
conductor(s) shall be connected in accordance with 250.32(B)
or (C). Where there is no existing grounding electrode, the
grounding electrode(s) required in 250.50 shall be installed.

Unless the exception applies-
Exception: A grounding electrode shall not be required
where only a single branch circuit, including a multiwire
branch circuit, supplies the building or structure and the
branch circuit includes an equipment grounding conductor
for grounding the normally non–current-carrying metal
parts of equipment.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I wonder if I should ground a welding shelter. The shelter is like a roofed structure on four columns. It doesn't have any walls. In the center of the shelter is the welding receptacles mounted on a unistrut.

are you asking if you need to ground the structure or the electrical system?
 