Neutral and Ground Bus Spacing

Status
Not open for further replies.

xguard

Senior Member
Location
Baton Rouge, LA
Is there a minimum distance that a grounding bus and neutral bus must be located from each other? The ones in question have a bout a 1/8" gap between them, metal to metal.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
408.56 has some information on this topic. But its associated table might not specifically address your question. It gives a minimum separation between live parts and ground, and your 1/8 inch is not sufficient. My question is whether we are to consider the neutral bus as being "live parts." This is, however, a moot issue, because of the exception that takes listed parts of panelboards out of the requirement.
 

jumper

Senior Member
408.56 has some information on this topic. But its associated table might not specifically address your question. It gives a minimum separation between live parts and ground, and your 1/8 inch is not sufficient. My question is whether we are to consider the neutral bus as being "live parts." This is, however, a moot issue, because of the exception that takes listed parts of panelboards out of the requirement.

Interesting idea to ponder. I want to say no, but......hmmmm.
 