detached fourplex property

Status
Not open for further replies.

bobbymari

Senior Member
Location
los angeles ca
So , we have a four unit bldg all bldgs detached from one another. Our meter section will be on rear bldg, all units fed underground. Question is this being that all units are detached would we treat each individual sub as its own "service" as far as grounding. I/e driving a rod for each detached unit tied in with each cold water entry and bond the neutral bar. Units power all originates at rear bldg with an egc along with their subfeeds.
Or do we treat it like a typical subfeed with isolated neutral bar
 

bobbymari

Senior Member
Location
los angeles ca
Or would it just simply get its own grounding electrode system at each detached unit ..ground rod tied in to cold water entry and leave neutral isolated to avoid parallel path of neutral return
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I think this is what you are looking for. :

250.32 Buildings or Structures Supplied by a Feeder(s)

or Branch Circuit(s).
(A) Grounding Electrode. Building(s) or structure(s)
supplied by feeder(s) or branch circuit(s) shall have a
grounding electrode or grounding electrode system
installed in accordance with Part III of Article 250. The
grounding electrode conductor(s) shall be connected in
accordance with 250.32(B) or (C). Where there is no
existing grounding electrode, the grounding electrode(s)
required in 250.50 shall be installed.
 

bobbymari

Senior Member
Location
los angeles ca
I think this is what you are looking for. :

250.32 Buildings or Structures Supplied by a Feeder(s)

or Branch Circuit(s).
(A) Grounding Electrode. Building(s) or structure(s)
supplied by feeder(s) or branch circuit(s) shall have a
grounding electrode or grounding electrode system
installed in accordance with Part III of Article 250. The
grounding electrode conductor(s) shall be connected in
accordance with 250.32(B) or (C). Where there is no
existing grounding electrode, the grounding electrode(s)
required in 250.50 shall be installed.

Thank you sir.
Equipment ground ran with feeders, ges at each detached bldg with isolated neutrals...
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
As long as there is a service disconnect ahead of the wire runs to each building, they are feeders. If there are only meters and no disconnect with OCPD, then they are still service conductors.
 

mgookin

Senior Member
Location
Fort Myers, FL
So , we have a four unit bldg all bldgs detached from one another. Our meter section will be on rear bldg, all units fed underground. Question is this being that all units are detached would we treat each individual sub as its own "service" as far as grounding. I/e driving a rod for each detached unit tied in with each cold water entry and bond the neutral bar. Units power all originates at rear bldg with an egc along with their subfeeds.
Or do we treat it like a typical subfeed with isolated neutral bar

Sounds to me like you have 4 - one unit buildings.

Am I reading that wrong?
 

kwired

Electron manager
Location
NE Nebraska
As long as there is a service disconnect ahead of the wire runs to each building, they are feeders. If there are only meters and no disconnect with OCPD, then they are still service conductors.
That is the key here - where is service disconnecting means?

Each separate building needs it's own grounding electrode system either way - it just connects to the grounded conductor if they are service supplied vs to the equipment grounding conductor if they are feeder supplied. Each separate building also needs, at or on the building, a disconnect (or up to six disconnects) regardless if service or feeder supplied. 2014 NEC did relax the rules on whether a feeder supplied disconnecting means needs to be suitable for use as service equipment though.
 

bobbymari

Senior Member
Location
los angeles ca
That is the key here - where is service disconnecting means?

Each separate building needs it's own grounding electrode system either way - it just connects to the grounded conductor if they are service supplied vs to the equipment grounding conductor if they are feeder supplied. Each separate building also needs, at or on the building, a disconnect (or up to six disconnects) regardless if service or feeder supplied. 2014 NEC did relax the rules on whether a feeder supplied disconnecting means needs to be suitable for use as service equipment though.

Got it, yes each unit will be fed from main multimeter section behind rear building with ocp so yes they will each be feeders not service and feeders will contain egc from the main service panel so we will be providing each unit with a grounding electrode system but isolating the neutrals at the subs so as not to have floating neutrals back to the gear..
Thank you all
 