Dear Team,
Please assist me as per the following explanations,
I spent last night and this morning stripping my systems apart to try and see if I could find any faults.
Can you please help me and advice testing/fault finding equipment to verify our equipment provided
1 X 33KV Ring Main Unit
1 X MVA Transformer
1 X 500KVA Transformer
Within the port we have a RMU distributing to 2 X Transformers, from these we have LV panels with a backup generator (change over switches in place).
When we are running through Utility
L1/N is showing 170V
L2 /N is showing 237V
L3/N is showing 359V
N/E is showing 117V
Running through generator
L1/N 241V
L2/N 237V
L3/N 239V
N/E 12V
This leads me to believe that there is a poor connection between our N and the incoming Transformers, this will mean our N is not held to our earth potential. This fault has only just developed, so we need to find the reason.
What can be the possible causes??
Please assist me as per the following explanations,
I spent last night and this morning stripping my systems apart to try and see if I could find any faults.
Can you please help me and advice testing/fault finding equipment to verify our equipment provided
1 X 33KV Ring Main Unit
1 X MVA Transformer
1 X 500KVA Transformer
Within the port we have a RMU distributing to 2 X Transformers, from these we have LV panels with a backup generator (change over switches in place).
When we are running through Utility
L1/N is showing 170V
L2 /N is showing 237V
L3/N is showing 359V
N/E is showing 117V
Running through generator
L1/N 241V
L2/N 237V
L3/N 239V
N/E 12V
This leads me to believe that there is a poor connection between our N and the incoming Transformers, this will mean our N is not held to our earth potential. This fault has only just developed, so we need to find the reason.
What can be the possible causes??