    #31
    splicing

    Originally posted by kwired View Post
    If the 2-2-2-4 was feeding entire dwelling unit it was acceptable per 310.15 (B)(7) to put it on a 100 amp breaker. They possibly were used to doing that frequently and knew it was acceptable but maybe not aware of why.

    But still a problem if you needed a 125 amp feeder. With (B)(7) and 125 amp - you are about 4 amps too much for #1 so 1/0 Aluminum is what would be required.
    Your contractor needs to replace that SER, are you sure he had a license???

    Comment


      #32
      Since this is becoming a DIYer thread I am closing it.

      Cubgirl, good luck with getting this resolved.

      Roger