Announcement
Collapse
No announcement yet.
Food Trailer Grounding
Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts
    Recently, our company set up a food trailer truck with 240V, single-phase, 3W system. When it was rolled out to sell, a kid accidentally experienced an electric shock. After the situation, it was found out that though all electrical equipment were provided with grounding and was connected to the generator's grounding system, the generator was not properly grounded. Also, jackets of some wires were damaged (perhaps because of wire pulling).
    With this, any recommendation for the effective grounding of our mobile food trailer?
    #2
    Do you have generator only?
    Or do you have generator plus utility connection?
    Do you have a circuit breaker panel in the truck (MDP)?
    Welcome to the forums.
    You make the lights come on and we make them go off.
    Comment
      #3
      If neither the truck, nor its electrical system, nor the generator were effectively grounded, the only way to develop a touch potential (to produce a shock) would be if some of the equipment had a current leak to earth ground or the kid touched two parts of the truck which were not bonded to each other.
      Needs analysis, not just grounding!
      Comment
        #4
        I agree.
        You need to know what two surfaces the boy touched and figure out why they were at different potential. There is probably more of a bonding issue here then a grounding issue I would guess. "Grounding" of the on board generator may not be required, bonding of non current carrying metal parts is required though.
        If set up for both on board power and to plug into a premises system, you may need to take a harder look at what is bonded to where and eliminate any neutral to ground connections you may have. There could be a combination of issues between the trailer and the premises wiring where it was plugged in as well.
        I live for today, I'm just a day behind.
        Comment
          #5
          if by grounding you mean some kind of grounding electrode (such as a ground rod), it is doubtful such a GE would be of any real value as far as reducing the chance of an electric shock.
          the non-current carrying metal parts should all be bonded together so there should not be any voltage potential between them.
          In any case, as someone else mentioned, there is no where near enough information available in the post to know what really happened or how to deal with it.
          Bob
          Comment
          Working...
          X