5 ohms or less

Status
Not open for further replies.

big john

Senior Member
Location
Portland, ME
Which assumes that the user of an integrated three point FOP tester actually runs a plot using different middle electrode positions instead of setting that probe at the "correct" distance and just reading the meter which pre-calculates the earth impedance based on an ideal voltage versus position plot.
Well, yeah, any test is fallible when it's done incorrectly. I know it's a common mistake, but I've never seen any literature that suggests only picking the 62% mark, and that's definitely not an IEEE test. Whereas you can do a clamp on test exactly like the instruction manual dictates and still get a wrong result.

One is a failure of methodology, which is fixable. The other is a failure of equipment, which ain't.
 