Equipotential Grounding Test Failing

Status
Not open for further replies.

Shujinko

Senior Member
I have a project in a hospital in a CT Scan Room where the equipotential grounding test is failing. It is only failing at the arm of the a multi joint arm mounted injector. The arm is mounted to a uni-strut structure above the ceiling. This uni-strut structure is grounded. However, the arm itself does not have it's own bonding conductor. Would the solution be just running a bonding conductor directly to the arm? Or could the actual mounting arm be an issue? Has anyone run into this? If so, how was it resolved? Thanks.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
We run into this type of situation pretty frequently. The way I handle it is I simply make a note on the report that the field installed wiring to the equipment has met the <.1 ohm requirement but the manufacturers equipment is --- ohms, then let them take it up with the AHJ. It is not a good idea to do any field modifications to any piece of medical equipment, the liability is way to great.