Removal of 3-wire branch circuits with new service?

Status
Not open for further replies.

ArcLazerbeam

Member
Location
VT
Hey Guys, been lurking around the forums for a while, found some great content which I appreciate. So thanks a bunch. I was hoping I could get some feed back or some help on a situation I was just in.

My boss and I did a new resi service and panel change out on a house built in the 70s. The existing setup had the first means of disconnect at the panel inside, but my boss (not thinking about it too much) bought a meter pack with a main breaker. So naturally I separated the grounds and neutrals inside when doing the panel up. But the inspector tried nailing us on re-using old 3-wire BCs for the range and dryer. It was stated that we couldn't go from a 3-wire to 4-wire back to a 3-wire (service conductors -> feeder to main panel -> branch circuits for range/dyer.) My boss said he overlooked that and should have known better, but I've never heard of a code article requiring the separation of such. Any ideas where I can find such a reference in NEC 2014? Or is he dead wrong. A tough pill to swallow being that the customers are already paying for a new service.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Take a look at (3).

Welcome to the forum. :)

250.140 Frames of Ranges and Clothes Dryers. Frames
of electric ranges, wall-mounted ovens, counter-mounted
cooking units, clothes dryers, and outlet or junction boxes
that are part of the circuit for these appliances shall be
connected to the equipment grounding conductor in the
manner specified by 250.134 or 250.138.
Exception: For existing branch-circuit installations only
where an equipment grounding conductor is not present in
the outlet or junction box, the frames of electric ranges,
wall-mounted ovens, counter-mounted cooking units,
clothes dryers, and outlet or junction boxes that are part of
the circuit for these appliances shall be permitted to be
connected to the grounded circuit conductor if all the fol-
lowing conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire;
or 208Y/120-volt derived from a 3-phase, 4-wire, wye-
connected system.
(2) The grounded conductor is not smaller than 10 AWG
copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded
conductor is uninsulated and part of a Type SE service-
entrance cable and the branch circuit originates at the
service equipment.

(4) Grounding contacts of receptacles furnished as part of
the equipment are bonded to the equipment.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
It depends if those neutrals are insulated or not. If they are bare (SEU) it must come out of the service, if its bare copper (NM) not code since day one, but if the neutral is insulated it may originate from a sub panel.
 

ArcLazerbeam

Member
Location
VT
Take a look at (3).

Welcome to the forum. :)

Thanks guys. That makes sense know that I think it through from a practical bonding point of view. I did a quick (and I mean quick) search on google about this but didn't get much. Wonder how often this isn't done when others were put in my scenario. Oh well. I want to be one of the good ones, hate breaking the code and always looking to improve, so you can bet I'll never forget this one.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Thanks guys. That makes sense know that I think it through from a practical bonding point of view. I did a quick (and I mean quick) search on google about this but didn't get much. Wonder how often this isn't done when others were put in my scenario. Oh well. I want to be one of the good ones, hate breaking the code and always looking to improve, so you can bet I'll never forget this one.

If the conductors have an insulated neutral then you don't need to change anything as they can come from a subpanel per the exception. But if they are SE cable with bare neutral then you would have to change to a 4-wire.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
If the conductors have an insulated neutral then you don't need to change anything as they can come from a subpanel per the exception. But if they are SE cable with bare neutral then you would have to change to a 4-wire.

To be clear- if the cable has an insulated neutral and a ground such as 10/3 or 6/3 NM.

-Hal
 

JFletcher

Senior Member
Location
Williamsburg, VA
Hey Guys, been lurking around the forums for a while, found some great content which I appreciate. So thanks a bunch. I was hoping I could get some feed back or some help on a situation I was just in.

My boss and I did a new resi service and panel change out on a house built in the 70s. The existing setup had the first means of disconnect at the panel inside, but my boss (not thinking about it too much) bought a meter pack with a main breaker. So naturally I separated the grounds and neutrals inside when doing the panel up. But the inspector tried nailing us on re-using old 3-wire BCs for the range and dryer. It was stated that we couldn't go from a 3-wire to 4-wire back to a 3-wire (service conductors -> feeder to main panel -> branch circuits for range/dyer.) My boss said he overlooked that and should have known better, but I've never heard of a code article requiring the separation of such. Any ideas where I can find such a reference in NEC 2014? Or is he dead wrong. A tough pill to swallow being that the customers are already paying for a new service.

Here, if they are not moved, they can stay. Move em (even shortening the original wire run) and you get to pull all new 4 wire circuits.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
To be clear- if the cable has an insulated neutral and a ground such as 10/3 or 6/3 NM.

-Hal

We're talking about existing 3-wire circuits to a stove or dryer. The exception allows the neutral to also be the EGC. But if the 3-wire has a bare neutral from a SE cable then it would have to originate from the main panel and not from a subpanel.
 