Grounding at main cabinet

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Older Type-NM cables have grounding conductors separated and secured to a screw in the top of the panel. Other grounding conductors are secured to the screw within the cabinet. I do not remember seeing this before... any advise?
 

Attachments

  • DSCF9272.jpg
    DSCF9272.jpg
    126.1 KB · Views: 0

jumper

Senior Member
I will take 110.14(A) for 100$ Alex.

Where is a bolt or screw identified as suitable for more than one conductor termination.

Yeah I know "identified" is subjective....I ain't seeing it myself.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I will take 110.14(A) for 100$ Alex.

Where is a bolt or screw identified as suitable for more than one conductor termination.

Yeah I know "identified" is subjective....I ain't seeing it myself.

Terminals for more than one conductor and terminals
used to connect aluminum shall be so identified.
a bolt is not a terminal. the code does not restrict how many wires can be connected to a bolt.
 