B-inspector
How do you bond a turnstile considering the moving parts?
If it must be bonded, a contact device like the brushes in wound rotor motors.
Too close to a pool?Why would I be bonding the moving parts of a turnstile?
what kind of turnstile?
I got the same reference brush earthing devices they use this system to bond train wheels to the tracks.
250.8 Connection of Grounding and Bonding Equipment.
(A) Permitted Methods. Grounding conductors and bond-ing jumpers shall be connected by one of the following means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
There are many reasons you bond fences and gates mostly for safety.
man gate full height turnstile.
If it is not NEC bonding I think its going to be tough to find those listed for grounding.
Of course those machines are listed as a complete assembly.