With two rods, as a technical Code requirement, the lateral looseness is not an issue. If there were only one rod, the requirement to verify the 25 Ohm resistance to Earth would lead the installer to ensure as good a contact with Earth along the length of the rod as possible.Kind of what I thought. I also grabbed the rods... seems to be some lateral movement at the top.
This is a new service for a very old home remodeled by a flipper. Does this look OK?
Does it look OK, nope. How could this possibly pass an electrical inspection?
Does it look OK, nope. How could this possibly pass an electrical inspection?
They are not buried thoughI'm guessing the green wire is smaller than #4, so it needs physical protection, a sleeve strapped to the wall. The ground rods need to have 8' in contact with earth, so they need to be below grade (assuming that is a standard 8 foot ground rod). The acorn clamps need to be listed for direct burial if they aren't.
They are not buried though
I do lots of work without inspections but it sure doesn't look like that. (It looks much worse.)
From your keyboard to His ears.
That is hack work.
Does it look OK, nope. How could this possibly pass an electrical inspection?
I'd step out on the limb and say they are not greater than 6' apart.
Does it look OK, nope. How could this possibly pass an electrical inspection?
My guess is no Inspection required because no permit was applied for. Not many Flippers will do anything to code unless forced and can get away with it. That phase locked loop was a nice touch.
Trip hazard is not mentioned. Physical protection is.It doesn't matter if they are 10' the code says the rod must be completely below grade. Definitely a trip hazard.
If the GEC is sized smaller than #4 solid it must be protected.
Sent from my LGLS991 using Tapatalk
(G) Rod and Pipe Electrodes.
The electrode shall be installed such that at least 2.44 m (8 ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10