bond gas pipe

Status
Not open for further replies.

sanfcarolyn

New member
Location
San Francisco CA
We would like to bond the gas pipe. Where should we attach the bonding clamp? The electrical main is ground to earth in the garage and also to the 1/2” portion of the copper water main in the hallway next to the garage. Last week Comcast (Xfinity) bonded the coax.
79E16602-6D12-443A-89B4-ED2856139B9D


F1DA9DDE-847B-4B87-9B49-A409936E4C01


D3790437-02CC-4513-93BC-F2420256E3BB

 
Unsure whether rules are the same everywhere but in NYS, bonding of the gas line is directed in the following manner:

1) Gas meter outside - Bond the first 6" of rigid pipe entering the premises to the GEC.

2) Gas meter inside - Bond on the customer side, after the di-electric union provided by the gas company, to the GEC.

As I have been led to understand, in this area, the gas company places a "cathodic signal" onto the gas piping system for corrosion reduction. Bonding a gas line improperly would effectively eliminate this anti-corrosion signal.
 